In LWT mode the circulation pump is activated every 3min 6 sec, wear and tear? #121

Answered by Arnold-n
buuhsmead asked this question in Q&A
Discussion options

You must be logged in to vote

To my knowledge this is normal if A2.1.9/[F-0D]=1, although in my system it is every 5 minutes. I do not think this is problematic, it's not the heat pump's compressor but only the circulation pump. However, it may be an indication that the system is "cycling" ("pendelen") which is not optimal for efficiency or compressor wear.

Replies: 1 comment

Comment options

You must be logged in to vote
0 replies
Answer selected by buuhsmead