Preventing or minimising defrost cycles? #142
Replies: 13 comments 9 replies
-
Hi @martindell - nice to hear from you again. Assuming you updated the ATmega firmware to 0.9.28 or later, you can request the Daikin to restart using the command L99 or (with recent firmwares) with HA button One way of minimizing defrosts is by reducing LWT when it is cold. In your message I am confused that the heat pump is running at all if you indicate that the house is not demanding any heat at all; could it be cycling due to LWT overshoot instead of due to defrosts? |
Beta Was this translation helpful? Give feedback.
-
Hi @Arnold-n I'm making progress. Connected OK via telnet, reset MQTT details, issued an L1 command and now I have control again - phew. Even though telnet works, I can't seem to update to the latest firmware:
Am I doing something dumb? The ESP-01 programmer will arrive tomorrow so I can try that instead |
Beta Was this translation helpful? Give feedback.
-
Well, I managed for 'fix' the symptom - but not the underlying problem. I set the minimum LWT to 20 and now the pump runs / samples but doesn't switch the compressor on - because the water temp is above 20. What's weird is that the pump is set to request mode but this sensor: sensor.s1_circulation_pump_onoff is set to 1 permanently and sensor.s0_heating_onoff = 1 even when LWT is OFF |
Beta Was this translation helpful? Give feedback.
-
I would recommend to set the LWT setpoint at 25C or above. If the LWT setpoint is below 25C, the compressor is never used - I do not think the Daikin manual warns explicitly about this but it is a small note below the operation range graphs in the installer reference guide. |
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
-
Yeah, my 4-04 = 2 :/ Nice idea though, I wonder what the values of 0 and 1 would do? No info in my installation manual
- found this online: 0- continuous, 1- intermittent, 2-no protection
…On Thu, 21 Nov 2024, 10:59 Arnold, ***@***.***> wrote:
Could it be related to pipe anti-frost protection? Usually this is off
([4-04]=2) on non-monoblock systems.
—
Reply to this email directly, view it on GitHub
<#142 (reply in thread)>,
or unsubscribe
<https://github.com/notifications/unsubscribe-auth/AAJLAIQJ65SRYT4IQK4TUDT2BW4KRAVCNFSM6AAAAABSC72VQ2VHI2DSMVQWIX3LMV43URDJONRXK43TNFXW4Q3PNVWWK3TUHMYTCMZTGUYDSMI>
.
You are receiving this because you commented.Message ID:
***@***.***>
|
Beta Was this translation helpful? Give feedback.
-
Spoke to a Daikin tech today and he confirmed that it is indeed an internal pipe-freeze thing. And it occurred to me that maybe my indoor unit doesn’t know what the temp is indoors - I ditched the Daikin thermostat years ago. Will check my settings when I get home. Update to the latest MQTT worked via the ESP-01. So many new sensors! I played a little bit with controlling DHW and LWT but the on/off commands didn’t seem to work every time. I restarted the device a few times but that didn’t seem to help. Are there any settings / logs I should check? |
Beta Was this translation helpful? Give feedback.
-
It is helpful to monitor MQTT topic P1P2/S/# or observe messages from a telnet session. Sounds like you are running out of write budget. |
Beta Was this translation helpful? Give feedback.
-
Ah, that makes sense - will do, thanks.
…On Fri, 22 Nov 2024, 18:03 Arnold, ***@***.***> wrote:
It is helpful to monitor MQTT topic P1P2/S/# or observe messages from a
telnet session. Sounds like you are running out of write budget.
—
Reply to this email directly, view it on GitHub
<#142 (comment)>,
or unsubscribe
<https://github.com/notifications/unsubscribe-auth/AAJLAISDQYHLB5QNQLDIBJD2B5PWBAVCNFSM6AAAAABSC72VQ2VHI2DSMVQWIX3LMV43URDJONRXK43TNFXW4Q3PNVWWK3TUHMYTCMZVGE2DGMQ>
.
You are receiving this because you commented.Message ID:
***@***.***>
|
Beta Was this translation helpful? Give feedback.
-
Mystery solved. I had a rogue setting for internal thermostat. I set 0c 7 to 1 and the pump cycling stopped. Thanks for your help @Arnold-n |
Beta Was this translation helpful? Give feedback.
-
@martindell I have a similar problem and followed this discussion. What do you mean with |
Beta Was this translation helpful? Give feedback.
-
Hi, in the installer settings on my unit, there's a set of cryptic settings
that Arnold exposes as field settings. On my one, page 0c, position 7 was
set to 2 - and I changed it to 1.
My hypothesis is that the unit had entered a pipe freeze prevention mode
because of the lower outside temperature.
Originally, my system had a Daikin room thermostat, but I replaced it last
year with smart thermostats and TRV's.
My guess is that the heat pump was running a frost prevention mode because
it no longer had a measurement for internal temperature.
Changing this setting was my best guess - and it seemed to work.
…On Mon, 25 Nov 2024, 08:35 savage7, ***@***.***> wrote:
@martindell <https://github.com/martindell> I have a similar problem and
followed this discussion. What do you mean with 0c 7 to 1 ?
—
Reply to this email directly, view it on GitHub
<#142 (comment)>,
or unsubscribe
<https://github.com/notifications/unsubscribe-auth/AAJLAIVJEBNGDQRWZOB4S532CLOO5AVCNFSM6AAAAABSC72VQ2VHI2DSMVQWIX3LMV43URDJONRXK43TNFXW4Q3PNVWWK3TUHMYTCMZWHE3DMMA>
.
You are receiving this because you were mentioned.Message ID:
***@***.***>
|
Beta Was this translation helpful? Give feedback.
-
Makes sense, to add: field setting 0c-7 (Daikin denotes this as [C-07], the P1P2MQTT setting starts with C_07 to avoid a minus signal in the name) relates to system control by either 0:LWT (always on), 1:external room thermostat (relays), or 2:room thermostat. Seems indeed that some protection is triggered by the combination of room thermostat mode and missing room temperature sensor. |
Beta Was this translation helpful? Give feedback.
-
It just got cold here (in the UK) and my Daikin Altherma spent the whole day cycling in and out of defrost cycles. Thanks to Arnold's magic P1/P2 solution - at least I can see what's happening. Comparing outside temperature and power draw on the compressor unit - it seems to be trying to preempt freezing up when temp drops below 2 degrees C. (Between 18:00 and 18:30 is when I experimented with blasting blast heat into the house - without much success.)
Comparing top chart (outdoor temp) with bottom chart (outdoor unit power), this waste of energy started between 10:00 and 10:30 when temp dropped - and carried on all day despite the house not demanding heat at all.
I'll take a look at the heat exchanger fins tomorrow to see if they're clean, but googling around, I came across this article about hacking Daikin's defrost cycles: https://harizanov.com/2012/02/defrost/
It relies on being able to reset the indoor unit (I think) before it starts defrosting. Finally, I have two questions:
Beta Was this translation helpful? Give feedback.