HA is showing 0 power on both my main phases, but voltage and frequency are fine. I have the CT's oriented properly with the 'To Breaker' arrow pointing down toward the breakers. I have the black wire going to a Phase A breaker and Red wire going to a Phase B breaker. Blue/white wires going to neutral/ground. I didn't change anything in that section of the default yaml config for the sensors except the 'name:' labels. The circuits all seem to be showing correct usage, just not phases or total. Am I missing something? I just reconnected the black and red wires and my Phase B is 52.4V / 8 angle / 2934W. Phase A showing 122V / 59.8Hz / 0W. |
Beta Was this translation helpful? Give feedback.
Replies: 3 comments 5 replies
-
I have the same issue. I finally added the Phases A-C (the individual ones work perfectly) and it shows blank 0 Watts on all of them. |
Beta Was this translation helpful? Give feedback.
-
Sounds like the top 2-3 Other than that, you can try removing the |
Beta Was this translation helpful? Give feedback.
-
I had to flip both the CT clamps around so breaker arrow was pointing toward outside and not down into the panel. |
Beta Was this translation helpful? Give feedback.
I had to flip both the CT clamps around so breaker arrow was pointing toward outside and not down into the panel.