I have three 3 phase panels that contain 19 circuits that I would like to monitor. The balanced two and three phase devices have one CT Sensor on only one leg whereas the unbalanced have a CT sensor on each leg. I am interested in knowing how much Wattage is being used by each of the 19 circuits and am not concerned about knowing the full usage of all three panels, so I figured I could use the 200A CT sensors just like I would the 50A Sensors. With the exemption of A, B, and C terminals (I still am not sure how to configure those in my YAML file, I have included the correct phase for each circuit. On a 220VAC single phase AC, one leg seems to be reading correctly, but the other is measuring 0. Why would that be? Additionally devices that are on seem to be pulling very low wattage (i.e. 3.5W for a 5 ton package unit with a multiplier of 3). What should I change in the YAML file to make terminals A,B,and C simply CT sensors and not use their data as a multiplier (if I can)? |
Beta Was this translation helpful? Give feedback.
Replies: 1 comment 3 replies
-
Do you mean the Are the voltage readings accurate? |
Beta Was this translation helpful? Give feedback.
Appreciate the extra data--this makes sense & looks right so far. I think I'm understanding the problem a little better--it kinda sounds like maybe the Vue is expecting a positive current reading (for the current to travel in the direction of the arrow on the clamp), but there's actually a negative reading.
What do you see when you replace
*pos
on the circuits with this issue with*invert
? Does the data look about right?