Low Total Reading and Low Phase R #289
-
This may be more of an installation issue, but my phase R values are always between -50 and 50 basically and my overall (when compared to the meter data) is up to 3x lower than it should be. Is this software/config issue on my part or have I installed something wrong? |
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 1 reply
-
Not sure what you're exactly saying, what is "phase R"? You mean "Red"? So you're talking about 1 of the main phases? You're saying that your power values for your main clamps are off? This happens with stock firmware too then, I assume? You did install in them in the right location, where utility enters your building? Maybe a photo of your setup? And your YAML file? |
Beta Was this translation helpful? Give feedback.
-
Anyway I understand, from reading the VUE3 thread, that you're using a VUE3. Just like that last guy there noted, I read there that you might need to change the CT port order, try that, so swapping the main CT's to a different port. |
Beta Was this translation helpful? Give feedback.
Yep, that's what it was: #264 (reply in thread)
Thank you.