Calculating Unmonitored Balance with Net Metering #308
Replies: 2 comments 4 replies
-
Assuming:
Your total energy consumed would be |
Beta Was this translation helpful? Give feedback.
-
Each phase has a regular When importing, Because of how this is split, to adjust the balance I need to add solar phases A and B and then subtract out the power return as well. I'd previously been including the solar phase A and B, which is clearly wrong.
I just pushed that update out and will see how it goes. |
Beta Was this translation helpful? Give feedback.
-
Good morning!
I converted my Vue 2 to esphome as part of my new solar installation, and am not quite sure how to properly get it to calculate the "balance", that consumed power which isn't monitored on a specific clamp. I also think I have Total Power and Total Power Return configured incorrectly, as I don't get any consumption read when I'm both consuming and contributing. It does seem to work correctly when I have no solar production and am only on grid, or when my total use is greater than solar production.
For example, currently I have:
Solar: 2367 W
Power Return: 1568 W
Total Power: 0 W
Balance: 0 W
Sum of all monitored circuits: 317 W
Thus, Total Power should be 799 W (Solar - Power Return) and Balance should be 482 W (Total - Monitored).
I did my best to assemble the config from the README and other posts here. Those together got me close, but I'm assuming I'm still missing something.
Here's my circuit and template configurations. I could fix up some of this in HA, I assume, but it seems more correct to fix this on the monitor itself.
I also have an issue with seeing small amounts of power, between 0 and 1 W, on circuits with no load, even when the breaker is off. From reading other posts, maybe this is a phase setting issue?
Appreciate an guidance. Thanks!